we recently repaired a 66 kV oil filled cable which was damaged by third party
Upon doing the final I/R test, the blue phase to earth reading was 92 M ohms. R and W phases were both in the range of 2.5 G ohms. the phase to phase readings were as follows R-W 3 G ohms , R-B and W-B 440 M ohms
The problem is that the oil pressure is remaining constant. hence there is no damage to the outer sheath. But the hidh resistance fault prevents a proper breakdown when doing the fault location, and the cable is buried appro 5-6 feet hence a very weak signal is recieved by the acoustic set. we even used the set to try and burn out the fault but the resultant was the I/R reading on the B phase went to 169 M Ohms. But it failed at 52 kV during the DC Hi-pot test. again the problem with detecting the fault.
any suggestions ???
your help is highly appreciated
prad
we recently repaired a 66 kV oil filled cable which was damaged by third party
Upon doing the final I/R test, the blue phase to earth reading was 92 M ohms. R and W phases were both in the range of 2.5 G ohms. the phase to phase readings were as follows R-W 3 G ohms , R-B and W-B 440 M ohms
The problem is that the oil pressure is remaining constant. hence there is no damage to the outer sheath. But the hidh resistance fault prevents a proper breakdown when doing the fault location, and the cable is buried appro 5-6 feet hence a very weak signal is recieved by the acoustic set. we even used the set to try and burn out the fault but the resultant was the I/R reading on the B phase went to 169 M Ohms. But it failed at 52 kV during the DC Hi-pot test. again the problem with detecting the fault.
any suggestions ???
your help is highly appreciated
prad