tranny
Electrical
- Jan 6, 2003
- 13
I recently experienced the failure of a 10 kVA constant voltage transformer utilized on the bypass side of a UPS that feeds a critical AC panel in a power plant. Here is what we experienced: At 11:00 AM someone smelled smoke from the SCADA cabinets. The doors were opened and a lot of smoke was coming from the power strips. (two power strips burned up, one tripped) Immediatly ran downstairs and found the 10 kVA constant voltage transformer (CVT) on fire. The circuit breakers were turned to the off position and the fire then subsided. Upon inspection of the CVT, it appeared that the inductor experienced a sigificant amount of heat from inside the core and coils, which then may have caused the insulation to fail. This may have then caused a voltage spike downstream causing a ground fault that wasn't cleared by the 175 A breaker.....for 10kVA at 120V, shouldn't this be a 90 A breaker anyway? (83.3 Amps) The fault current increased until stuff started catching on fire. I do not know if the system was in bypass when the failure happened, or if a failure at the power strip caused an overload on the inverter, which then caused it to switch to the bypass source. Can anyone provide some insite as to what may have happened. These constant voltage transformers utilize one or two inductor windings and capacitiors. Why are there two inductor windings, one bigger than the other?