hi, i'm starting this thread because I'm in a design dilemma and also for others who face similar design issues.
____________________________________________________________________________________________________________________________
Just let me get excerpts from my report up here:
REPORT BRIEF
The site visit was incepted to conduct an inspection following a reported fault in an air-conditioning system. The operation of three air-conditioners (2 x 50% duty) has resulted in water condensate forming on the ceiling surfaces, which if not resolved will result in damage of equipment....
Main Air-conditioning Issue
The operation of three air-conditioners (2 x 50% duty) has resulted in water condensate forming below and above the ceilings for each of the two rooms. The severity of the condensation issue was greater in the ATC Room.
To date, equipments in the ATC Room are operating at a required controlled temperature of 22°C. the Contractor has reported that when the room’s temperature reading was 24°C, the ATC equipment began to overheat.
Certain attempts have been made by the Contractor's staff to manage and mitigate the prevailing condensation issue:
a) Thickness of condensate pipe insulation was increased, which did little to improve the situation. Drops of condensate water still formed on the insulation’s outer surface.
b) Turning off of one duty air-conditioner, which resulted in equipment overheat.
c) Placing ply-wood planks above the “roof-less” electronic equipment to prevent drips of condensate water from entering the equipment, as a temporary solution.
Other Information:
1. The ceiling panels (possibly asbestos) rested on metal (possibly galvanized iron) frames. Condensation occurred on the surfaces of these frames. Subsequently, the edges of the ceiling panels were damaged and more importantly, water condensate on these surfaces dripped onto the ATC equipment. The lower-roof directly above the M&E Services and ceiling panels were made from a ‘special’ fire-fighting composite described by the fire dept which consists of ply-wood and polymeric material:
2. The compressor units for all 6 units were isolated in a well ventilated room on the lower roofs, and it is assumed that the source of water dripping was indeed condensation and not leakage due to equipment defect.
3. Even the bolts which held the ceiling-exposed air-con units to the ceiling had condensate forming on them.
4. Layout of ATC Room:
'Special fire-fighting material'
---------------------------------------------
M&E services area (i think around 29 degrees C)
---------------------------------------------
Ceiling panels
---------------------------------------------
ATC Room, Temp = {18,22} degrees C. dimensions: 10m x 7.5m x 3m.
---------------------------------------------
5. Equip Spec:
ATC Room: 3 ceiling exposed units (2 duty 1 standby) of ACSON A5CM 62C, capacity 55,000 btu/hr (6.41kW)
Central Control Room: 3 ceiling exposed units (2 duty 1 standby) of ACSON A5CM 50D, capacity 43,000 btu/hr (4.70kW)
____________________________________________________________________________________________________________________________
Question:
As i described the scenario above,
The room MUST be kept cold (22 degrees and below) but if it's too cold, condensation forms on the ceilings and end up damaging the equipment anyway. That's the dilemma.
What would be a feasible solution which is still relatively economical? Localising the cooling area? Setting up an exhaust fan in the M&E Services space to convect air in/out?
Thanks.
____________________________________________________________________________________________________________________________
Just let me get excerpts from my report up here:
REPORT BRIEF
The site visit was incepted to conduct an inspection following a reported fault in an air-conditioning system. The operation of three air-conditioners (2 x 50% duty) has resulted in water condensate forming on the ceiling surfaces, which if not resolved will result in damage of equipment....
Main Air-conditioning Issue
The operation of three air-conditioners (2 x 50% duty) has resulted in water condensate forming below and above the ceilings for each of the two rooms. The severity of the condensation issue was greater in the ATC Room.
To date, equipments in the ATC Room are operating at a required controlled temperature of 22°C. the Contractor has reported that when the room’s temperature reading was 24°C, the ATC equipment began to overheat.
Certain attempts have been made by the Contractor's staff to manage and mitigate the prevailing condensation issue:
a) Thickness of condensate pipe insulation was increased, which did little to improve the situation. Drops of condensate water still formed on the insulation’s outer surface.
b) Turning off of one duty air-conditioner, which resulted in equipment overheat.
c) Placing ply-wood planks above the “roof-less” electronic equipment to prevent drips of condensate water from entering the equipment, as a temporary solution.
Other Information:
1. The ceiling panels (possibly asbestos) rested on metal (possibly galvanized iron) frames. Condensation occurred on the surfaces of these frames. Subsequently, the edges of the ceiling panels were damaged and more importantly, water condensate on these surfaces dripped onto the ATC equipment. The lower-roof directly above the M&E Services and ceiling panels were made from a ‘special’ fire-fighting composite described by the fire dept which consists of ply-wood and polymeric material:
2. The compressor units for all 6 units were isolated in a well ventilated room on the lower roofs, and it is assumed that the source of water dripping was indeed condensation and not leakage due to equipment defect.
3. Even the bolts which held the ceiling-exposed air-con units to the ceiling had condensate forming on them.
4. Layout of ATC Room:
'Special fire-fighting material'
---------------------------------------------
M&E services area (i think around 29 degrees C)
---------------------------------------------
Ceiling panels
---------------------------------------------
ATC Room, Temp = {18,22} degrees C. dimensions: 10m x 7.5m x 3m.
---------------------------------------------
5. Equip Spec:
ATC Room: 3 ceiling exposed units (2 duty 1 standby) of ACSON A5CM 62C, capacity 55,000 btu/hr (6.41kW)
Central Control Room: 3 ceiling exposed units (2 duty 1 standby) of ACSON A5CM 50D, capacity 43,000 btu/hr (4.70kW)
____________________________________________________________________________________________________________________________
Question:
As i described the scenario above,
The room MUST be kept cold (22 degrees and below) but if it's too cold, condensation forms on the ceilings and end up damaging the equipment anyway. That's the dilemma.
What would be a feasible solution which is still relatively economical? Localising the cooling area? Setting up an exhaust fan in the M&E Services space to convect air in/out?
Thanks.