shotgunner
Electrical
- Dec 10, 2001
- 4
I was currently troubleshooting a problem with the Main Network Server at the company I work for. The UPS System would go into Battery Back-up several times in a 5 minute or so span and then the Server would shutdown (major head aches and death threats also occured whenever this happened). I put a Fluke 43B Power Quality Meter on the incoming designated cicuit to this Server and found that every 35 seconds, an inrush of current would appear and the line voltage would drop from 120 volt to 102 volts. I am assuming that the UPS System can condition the power supply + or - 5% (I can not find a manual on this server)so I can understand why the Server keeps going into battery back-up because the voltage drop is out of the + / - 5% range. I disconnected the Server from the UPS and our Server is running fine for the last two days even though the voltage drop is still present. My question is what could be causing the Server to initiate such a current rise / voltage drop this large every 35 seconds. Any tips or help would be greatly appreciated as I would like to have UPS back-up for this server