I am looking for other peoples interpretation of section 2305.1.5 of the IBC 2000 regarding use of plywood shearwalls... then compare that section to 2305.3.1.
Section 2305.1.5 rather clearly states that "Wood shear walls,... shall not be used to resist horizontal seismic forces contributed by masonry or concrete construction in structures over one story in height. (some exceptions)
Section 2305.3.1 states "Wood shear walls are permitted to resist horizontal forces in vertical distributing or resisting elements, provided the deflection..."
I would like to give a scenerio and apply these two sections. A four story multi-family building over a parking garage. Bad soil conditions results in a larger seismic force in a very low seismic area. The construction is composite steel joist with a 3" concrete deck (all floors). Walls are light gauge steel, sheathed with plywood on all exterior walls. X-braces "tension straps only" will be utilized, however, in only one direction of the building. The other direction has many openings and a perforated shear walls yielded better results.
Is this a code violation?
Also, any one see problems mixing the two lateral resistive systems?
Thanks
Section 2305.1.5 rather clearly states that "Wood shear walls,... shall not be used to resist horizontal seismic forces contributed by masonry or concrete construction in structures over one story in height. (some exceptions)
Section 2305.3.1 states "Wood shear walls are permitted to resist horizontal forces in vertical distributing or resisting elements, provided the deflection..."
I would like to give a scenerio and apply these two sections. A four story multi-family building over a parking garage. Bad soil conditions results in a larger seismic force in a very low seismic area. The construction is composite steel joist with a 3" concrete deck (all floors). Walls are light gauge steel, sheathed with plywood on all exterior walls. X-braces "tension straps only" will be utilized, however, in only one direction of the building. The other direction has many openings and a perforated shear walls yielded better results.
Is this a code violation?
Also, any one see problems mixing the two lateral resistive systems?