Gentleman... try to check this out...
This is taken from Design of Wood Structures - ASD by Donald E Breyer et al...fifth edition based on IBC 2003 pg 2.37
"The design overturing moment (0M) is the difference between the gross OM and 60 percent of the resisting moment (RM). The IBC requires that 0.6 X RM be greater than the OM. In other words, a factor of safety (FS) of 5/3 or 1.67 is required for overturning stability. Notice that in this stability check, an overestimation of dead load tends to be unconservative (normally an overestimation of loading is considered conservative). To obtain the design OM, 60 percent of the RM is subtracted from the gross OM. Up to this point, the DL being used in the calculation of RM did not include the weight of the foundation.
Now, if the design OM is a positive value (i.e., the gross OM is more than 60 percent of the RM), the structure will have to be tied to the foundation. The design OM can be replaced by a couple (T and C). The tension force T must be developed by the connection to the foundation. This tension force is also known as the design uplift force. If the design OM is negative (i.e. , the gross OM is less than or equal to 0.6 x RM), there will be no uplift problem. Should an uplift problem occur, 60 percent of the DL of the foundation plus 60 percent of the DL of the building must be sufficient to counteract the gross OM"
Hope this can clear some confussions on the above topic...
nrguades