jtse
Structural
- Nov 8, 2016
- 6
Is there anything in IBC that explicitly links the Chapter 3 occupancy classifications to the Chapter 16 live loads?
I'm working on an old concrete building (2-way flat slab with drop panels) that has no existing drawings. It's currently office space and will be renovated, but will remain an office building. There are new layouts, including larger conference / meeting rooms, which the architect is classifying as "Assembly" areas on their life safety sheets per IBC Chapter 3. They want us to demonstrate the floor has capacity for 100 psf un-reducible live load to meet the 'assembly' requirements of Table 1607.1. Per the question above, is that truly intended/required by Code? Are we permitted to still classify it as 'office' with 50+15 live load to match its current use, in spite of the life safety designation?
As it's an existing building with no drawings, we're having difficulty analyzing accurately. We've done concrete testing including coring & crushing, exposing some bar, and GPR scanning. Unfortunately, the inaccuracy of GPR data for bar sizes and depths within the slab limits capacity in the analysis. We suggested keeping the classification as office to justify it as an existing building - successfully performing for many years, no change in load - but the architect is concerned by the difference in designations.
I suspect many/most engineers design office floors for 50+15 psf live load (or 80 psf to cover corridors) across the full building footprint, ignoring any areas an architect may be labeling as 'assembly' space. The current layout obviously has corridors and some larger conference rooms, but in different areas than in the proposed renovation. I strongly doubt the current layout was set to place corridors / meeting rooms in areas of higher structural capacity. Given that it's an office building now, has been for many years, and will remain one, saying it needs additional capacity now will be difficult to justify.
I have been unable to find anything in IBC, its commentary, or online addressing this subject. Has anyone come across any references that speak to the question?
We're also looking for other paths to solve this. We proposed posting load / occupancy limits in the areas of the building where the otherwise Code-required live load can't be demonstrated by analysis (i.e. large conference rooms). I don't know of a code provision that discusses this idea - does anyone else? We're also looking at load testing. I'm concerned about doing this with a flat 2-way slab with drop panels (punching shear) - has anyone done that before?
Thank you!
I'm working on an old concrete building (2-way flat slab with drop panels) that has no existing drawings. It's currently office space and will be renovated, but will remain an office building. There are new layouts, including larger conference / meeting rooms, which the architect is classifying as "Assembly" areas on their life safety sheets per IBC Chapter 3. They want us to demonstrate the floor has capacity for 100 psf un-reducible live load to meet the 'assembly' requirements of Table 1607.1. Per the question above, is that truly intended/required by Code? Are we permitted to still classify it as 'office' with 50+15 live load to match its current use, in spite of the life safety designation?
As it's an existing building with no drawings, we're having difficulty analyzing accurately. We've done concrete testing including coring & crushing, exposing some bar, and GPR scanning. Unfortunately, the inaccuracy of GPR data for bar sizes and depths within the slab limits capacity in the analysis. We suggested keeping the classification as office to justify it as an existing building - successfully performing for many years, no change in load - but the architect is concerned by the difference in designations.
I suspect many/most engineers design office floors for 50+15 psf live load (or 80 psf to cover corridors) across the full building footprint, ignoring any areas an architect may be labeling as 'assembly' space. The current layout obviously has corridors and some larger conference rooms, but in different areas than in the proposed renovation. I strongly doubt the current layout was set to place corridors / meeting rooms in areas of higher structural capacity. Given that it's an office building now, has been for many years, and will remain one, saying it needs additional capacity now will be difficult to justify.
I have been unable to find anything in IBC, its commentary, or online addressing this subject. Has anyone come across any references that speak to the question?
We're also looking for other paths to solve this. We proposed posting load / occupancy limits in the areas of the building where the otherwise Code-required live load can't be demonstrated by analysis (i.e. large conference rooms). I don't know of a code provision that discusses this idea - does anyone else? We're also looking at load testing. I'm concerned about doing this with a flat 2-way slab with drop panels (punching shear) - has anyone done that before?
Thank you!