My current project (building code: IBC 2009) requires fall arrest D-ring anchors to be post-installed in a concrete wall. When I researched fall arrest anchors, I found many that are compliant with OSHA 1926, but cannot find any that are compliant with IBC 2009, or any version of IBC for that matter. The ICC website confirms this, as all of the ESR reports listed on their website are for structural anchors, not necessarily life safety. This is a little confusing, especially since I cannot find any exception in IBC 2009 or ACI 318-08 that excludes fall arrest systems. In fact, Section D2.1 of ACI 318 states right up front that safety related devices are inclusive: "Appendix D is restricted in scope to structural anchors that transmit structural loads related to strength, stability, or life safety."
So, are there really no options for post-installed anchors for fall arrest systems, or is there some language in IBC or ACI that defaults approval to OSHA in lieu of ICC for safety system anchorage? Even if that were the case, the suppliers would then be able to advertise that their anchors are IBC compliant as well as OSHA compliant, which they do not. IBC does state in Section 1703 that approval comes from an approved agency, but it is not clear to me if an anchor is OSHA-approved that it does not need to be ICC-approved. Any thoughts?