We have a project where we are adding new RTU's and replacing the existing roof with increased insulation. During our analysis of the roof for the new RTU's, it was determined that the ground snow load increased from 40 PSF to 50PSF in the mid 2000's (we are in a site specific location). The original building was built in the early 1970's and based on the sizing of the roof members, the flat roof snow load was lower than 28 psf.
Per the IEBC, analysis is only required where the "alterations cause an increase in design dead, live or snow load, including snow drift effects, of more than 5% shall be replaced or altered as needed to carry the gravity loads required by the International Building Code for new structures." If the increase in insulation adds less than 5% more dead load, can it be justified that the structure not impacted by the RTU does not need to be reinforced to resist the increased snow load due to the changing code? In other words, can the increase in snow load be ignored since the increased loading is not caused by the alterations, but by a change in the code.
Per the IEBC, analysis is only required where the "alterations cause an increase in design dead, live or snow load, including snow drift effects, of more than 5% shall be replaced or altered as needed to carry the gravity loads required by the International Building Code for new structures." If the increase in insulation adds less than 5% more dead load, can it be justified that the structure not impacted by the RTU does not need to be reinforced to resist the increased snow load due to the changing code? In other words, can the increase in snow load be ignored since the increased loading is not caused by the alterations, but by a change in the code.