Adam1980
Electrical
- Feb 17, 2012
- 87
Dear all,
concerning the current carrying capability of three-single core cables in trefoil in 9 way (3 x 3) duct bank and following the procedure in IEC 287 - 1 -1 and 287 - 2 - 1
when we are calculating T4 = T'4 + T"4 + T"' 4
T'4 is according to 287-2-1 2.2.7.1
T"4 is according to 287-2-1 2.2.7.2
T'" 4 is according to 287-2-1 2.2.7.3 and 2.2.3.2 considering the mutual effect of the other cables laid in the other ducts
The question is for T'"4 should we use 2.2.4.3.1 instead of 2.2.3.2?
that is use: (1.5/pi) x rho concrete x [ln(2u x (d'p/dp...)) - 0.630] instead of (1/(2 x pi)) x rho concrete x ln[(u - squareroot(u^2 - 1)) x (d'p/dp...)]
Thank you,
Adam
concerning the current carrying capability of three-single core cables in trefoil in 9 way (3 x 3) duct bank and following the procedure in IEC 287 - 1 -1 and 287 - 2 - 1
when we are calculating T4 = T'4 + T"4 + T"' 4
T'4 is according to 287-2-1 2.2.7.1
T"4 is according to 287-2-1 2.2.7.2
T'" 4 is according to 287-2-1 2.2.7.3 and 2.2.3.2 considering the mutual effect of the other cables laid in the other ducts
The question is for T'"4 should we use 2.2.4.3.1 instead of 2.2.3.2?
that is use: (1.5/pi) x rho concrete x [ln(2u x (d'p/dp...)) - 0.630] instead of (1/(2 x pi)) x rho concrete x ln[(u - squareroot(u^2 - 1)) x (d'p/dp...)]
Thank you,
Adam