Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

IEEE 142 calculations

Status
Not open for further replies.

heberovchem

Electrical
Oct 14, 2008
10
Could someone show me the calculations to arrive at the following percentages:
The available ground-fault current should be at least 25% (X0 = 10X1) and preferably 60% (X0 = 3X1) of the three-phase fault current to prevent serious transient overvoltages. Available is considerably higher than the level of fault current desirable in a resistance grounded system.
Thank you
 
Replies continue below

Recommended for you

Sorry, heberovchem, but how your question is related to IEEE 142?
 
It is written on page 16. But I've already figured out. Thank you.
 
Hi heberovchem. can you let me know what did you find?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor