1
- #1
crjohnson
Electrical
- Mar 31, 2017
- 3
Hi Folks,
I think I may have found an inconsistency in IEEE 242-2001 between the equations Section 9.5.2.4 and Table 9-6.
I hope that I am making a mistake somewhere, and y'all will be able to help point out my error.
Edit: I believe if you follow just the equation for any value of K other than 1, the equation results are way off. For values of k<1, you could overestimate the amount of current the cables could handle by a factor of 2 or more.
Based on the standard, values in table 9-6 are calculated based on the equation shown in 9.5.2.4:
However, if you plug in the values as indicated the results returned do not equal that of the table.
For example, take first line of table 9-6 calculated for EPR-XLP with T[sub]e[/sub]=130, T[sub]n[/sub]=90,and T[sub]o[/sub]=40
From the table:
But, if you change the equation to divide by k instead of multiply by k then it appears to work.
From Equation as corrected:
Does the corrected equation work for y'all?
Did I miss somewhere in the section where is says the inverse of K should be used?
I attached my spreadsheet where I ran my tests.
Thanks,
Chris
I think I may have found an inconsistency in IEEE 242-2001 between the equations Section 9.5.2.4 and Table 9-6.
I hope that I am making a mistake somewhere, and y'all will be able to help point out my error.
Edit: I believe if you follow just the equation for any value of K other than 1, the equation results are way off. For values of k<1, you could overestimate the amount of current the cables could handle by a factor of 2 or more.
Based on the standard, values in table 9-6 are calculated based on the equation shown in 9.5.2.4:
I[sub]e[/sub]/I[sub]n[/sub] % = SQRT(((T[sub]e[/sub]-T[sub]o[/sub])/(T[sub]n[/sub]-T[sub]o[/sub])-e[sup](-Θ*K)[/sup])/(1-e[sup](-Θ*K)[/sup])*((230+T[sub]n[/sub])/(230+T[sub]e[/sub])))*100
Where:I[sub]e[/sub] is emergency operating current rating,
I[sub]n[/sub] is normal current rating,
T[sub]e[/sub] is conductor emergency operating temperature,
T[sub]n[/sub] is conductor normal operating temperature,
T[sub]o[/sub] is ambient temperature,
K is a constant, dependent on cable size and installation type (see Table 9-5 in IEEE 242-2001),
230 is zero-resistance temperature value (234 for copper, 228 for aluminum),
e is base for natural logarithms.
I[sub]n[/sub] is normal current rating,
T[sub]e[/sub] is conductor emergency operating temperature,
T[sub]n[/sub] is conductor normal operating temperature,
T[sub]o[/sub] is ambient temperature,
K is a constant, dependent on cable size and installation type (see Table 9-5 in IEEE 242-2001),
230 is zero-resistance temperature value (234 for copper, 228 for aluminum),
e is base for natural logarithms.
However, if you plug in the values as indicated the results returned do not equal that of the table.
For example, take first line of table 9-6 calculated for EPR-XLP with T[sub]e[/sub]=130, T[sub]n[/sub]=90,and T[sub]o[/sub]=40
From the table:
k=0.5, %=1136
k=1.0, %=1602
k=1.5, %=1963
k=2.5, %=2533
From Equation as written:k=1.0, %=1602
k=1.5, %=1963
k=2.5, %=2533
k=0.5, %=2265.49
k=1.0, %=1603.885
k=1.5, %=1311.5
k=2.5, %=1018.061
k=1.0, %=1603.885
k=1.5, %=1311.5
k=2.5, %=1018.061
But, if you change the equation to divide by k instead of multiply by k then it appears to work.
I[sub]e[/sub]/I[sub]n[/sub] % = SQRT(((T[sub]e[/sub]-T[sub]o[/sub])/(T[sub]n[/sub]-T[sub]o[/sub])-e[sup](-Θ/K)[/sup])/(1-e[sup](-Θ/K)[/sup])*((230+T[sub]n[/sub])/(230+T[sub]e[/sub])))*100
From Equation as corrected:
k=0.5, %=1136.859
k=1.0, %=1603.885
k=1.5, %=1962.765
k=2.5, %=2532.281
k=1.0, %=1603.885
k=1.5, %=1962.765
k=2.5, %=2532.281
Does the corrected equation work for y'all?
Did I miss somewhere in the section where is says the inverse of K should be used?
I attached my spreadsheet where I ran my tests.
Thanks,
Chris