Thanks for the support Marke.
The sets that I was installing were residential with A/C loads.
The first tranche, (spec'ed by others.) were single phase, NA, self excited (with a brushless exciter, not capacitor excitation.)
All (about 6.) were 17 KVA and all were too smell.
At each install,the owner and myself would experiment with starting various A/C units to determine which and how many A/C units could be started successfully.
In every case, a 3:1 ratio of set KVA to A/C KVA was acceptable.
Then I would disable automatic starting so that the customer could control which and how many A/C units could be running.
Occasionally there would be one large A/C unit that was a 2.5:1 ratio, and that could be used and the 2.5:1 ratio used only if this was the first A/C too start.
My ultimate limit was the Automatic Transfer Switch contactor.
I was called in to repair a couple of installations done by others.
Too much load automatically starting and the voltage drop would drop out the standby contactor in the ATS.
With no load, the set would accelerate and the voltage would recover.
The contactor would pull back in.
Rinse and repeat.
It took a minute or so to destroy the ATS contactor.
At a 3:1 ratio, I never had a problem or a customer complaint.
Interestingly, I eventually came across the Cat sizing software.
Using the Cat default settings, all of about 20 installs failed as set too small.
After changing the default voltage drop value in the software to a more liberal value,all installs passed.
Had a set been sized to Cat specs, the customer would have started one more A/C and we would be back to the 3:1 factor.
A further note: The 3:1 ratio applies to Standby rated sets.
The KVA of a Prime rated set may be increased by 10% before applying the 3:1 factor,
By definition, a prime rated set plus 10 percent equals the standby rating.
I am willing to bet that the authors of IEEE 399 have never actually commissioned a standby gen-set "In the Wild".
--------------------
Ohm's law
Not just a good idea;
It's the LAW!