If a hydro unit is back charged in 2

Status
Not open for further replies.

Devendra Kumar

Electrical
Nov 28, 2022
4
If a hydro unit is back charged in standstill condition by malfunctional closing of 400kv Circuit Breaker ? What protection must operate?
 
Replies continue below

Recommended for you

If the unit is provided with Reverse power / Anti-motoring protection, it will operate.
When the machine is accidentally energised, the Excitation is OFF. So, Field failure protection is another one that could operate.
The new machines often are provided Protection against Accidental energisation. If the subject unit has this, then this will be the fastest one to operate.
 