I'm trying to permit a small storage shed (12ft x 52ft, Occupancy S, Construction Type IV) not an occupied space, and need to address energy code. How do I work through this within the energy code? I don't see that it addresses unconditioned spaces.
Can you clarify the code you are referencing? I assume ICC but please confirm. Also, what year is being referenced for your AHJ?
Thank you for your review.
Wahsington State (Pierce county) referecnes IECC 2021.
Section C202
Climate zone 4C Pierce County
So C402-406, C408 or C407
C402.1.1
That gets you out of the envelope requirements.
I do not know your ventilation and lighting requirements, but you would need to work through sections C403-C405
C406 is where you get your credits. You should be able to get 9 fairly easy if you work through C405 for lighting.
thank you! I will work throught these other sections.