At most industrial (and even commercial) installations I've seen, IMC is generally not used. They either select EMT for light duty, or RGS (rigid galvanized steel) for heavy duty. The philosophy being that if the environment is abusive enough to warrent IMC or RGS, they might as well put in RGS, given the relatively low difference in cost of IMC and RGS. RGS will withstand a blow from the proverbial fork-truck much better than IMC.
So far as I know, NEC treats IMC and RGS essentially interchangeably, whereever one is permitted, the other is OK too. I'm pretty sure that even applies to hazardous explosive installations (although you might wanna double check that).
So all in all, it really comes down to your environment, your personal preference, and your budget.
Beware, lots of IMC is aluminum -- obviously, if you're in concrete, you don't want any aluminum.