Impedance Grounded Systems 1

Status
Not open for further replies.

CuriousElectron

Electrical
Jun 24, 2017
182
0
0
US
Hello Gents,
I read a technical article that states, "In an impedance-grounded system, the neutral reference can be offset from center..".
Does anyone know why this would be the case or can point to a technical resource where this would be explained?

Thank you,
EE
 
Replies continue below

Recommended for you

It depends what the reference point is. Any current through the grounding impedance will cause a voltage drop between the wye point and the ground. This voltage drop, will cause a neutral shift, relative to a ground reference.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 