If the capacitance sensor is of the type of a variable capacitance sensor then you would recalibrate it
for different liquids. But, if the capacitance sensor is of multielectrode capacitance sensor type there is no need for calibration. More advanced microprocessor-based units are self-calibrating; sensitivity and time delay adjustments are under pushbutton control. These units are often supplied with self-test capability and built-in temperature compensation.
If the sensor is SS [stainless steel] made no coating is necessary.
In case where the liquid is highly conductive or corrosive then capacitance probes typically are coated with PFA[Teflon PFA] or PTFE[Teflon], Kynar, or polyethylene.
But, even in case of PTFE [Teflon] coating, the thin film of this dielectric material does not produce an important error in level measurement.
Some point level sensors are available with build-up immunity, or coating rejection functionality. This is required when the process material is wet or sticky and likely to cause permanent coating. Build-up immunity is provided by the addition of a second active section of probe and a second insulator.
I don’t know why it is necessary to measure the liquid specific resistance, but as I know from test of HV electric machine insulation it is possible to measure tangent-delta= Xc/R and so one may appreciate the resistance.
See:
Regards