In performing a short circuit calculation for verification of the rating of some installed switchgear, the result reflected equipment with a AIC below the calculated available. I have included the typical impedance elements, but would like to include more, to somewhat validate the equipment so as not to require replacement.
Does anyone have a reference for impedances of mechanical or compression type conductor terminations and bolted bus connections? Also references for the impedance of ANSI power circuit breaker contacts. They are obviously not zero, and are based on the installers capabilities.
With the "non-typical" (although real life) impedances included in the calculation, I believe the equipment will be properly rated per my calcs.