Have a 12MW utility-parallel, enclosed generator that is suddenly producing a very significant "hot electrical" smell.
All instruments are reporting "normal" values for temperature, current, voltage, etc. No protection has operated.
Did winding resistance and insulation resistance on both windings, plus surge on the stator. The only unexplainable reading is the rotor resistance was about 25% low based on nameplate voltage and current. The two caveats are the resistance is NOT temperature corrected, and this is a 28 pole machine so one shorted pole would not account for that much difference.
The rotor is basically inaccessible. You can barely even see it, so there's no way to do pole-drop.
Any suggestions at all for further testing? Something is going to fail here, and I have no idea how else to find it.
All instruments are reporting "normal" values for temperature, current, voltage, etc. No protection has operated.
Did winding resistance and insulation resistance on both windings, plus surge on the stator. The only unexplainable reading is the rotor resistance was about 25% low based on nameplate voltage and current. The two caveats are the resistance is NOT temperature corrected, and this is a 28 pole machine so one shorted pole would not account for that much difference.