Seems like this question comes up a lot in Arc Flash. Just looking for a better more consistent answer.
How do you determine if you "Include Main" or "Exclude Main"? We deal with a Client that has a standard that clearly states: Exclude the Main in the arc flash at an MCC. But there are others exact opposite. The wires come in, land directly on the Main Breaker, seems downstream should be protected. I thought that's why we included the Main breaker.
I understand the barrier argument too. There's a physical barrier between the Main compartment and the rest of the MCC - then you can include the main. What makes a barrier? There's going to be an opening between the Main section and rest of the lineup.
How do you determine if you "Include Main" or "Exclude Main"? We deal with a Client that has a standard that clearly states: Exclude the Main in the arc flash at an MCC. But there are others exact opposite. The wires come in, land directly on the Main Breaker, seems downstream should be protected. I thought that's why we included the Main breaker.
I understand the barrier argument too. There's a physical barrier between the Main compartment and the rest of the MCC - then you can include the main. What makes a barrier? There's going to be an opening between the Main section and rest of the lineup.