In-wall, low voltage wiring requirements

Status
Not open for further replies.

stel

Electrical
Sep 14, 1999
6
Is it necessary to use UL listed wiring when installing low voltage wiring (CAT5, Coax, speaker, etc.) in the walls of a home under construction? Can I just use the less expensive variety that is not UL listed?
 
Replies continue below

Recommended for you

Specifically check articles 800 through 830. There are other concerns besides voltage and ampacity such a flame spread.
 
All Electrical equipment must be approved for the purpose.
See Article 100, 110, 110-3b. Approved for the purpose means acceptable to The Authority Having Jurisdiction.
Its your license!
 
i was just called on this one by an overly nitpicky inspector. he cited nec110-3b disallowing my removing of the sheathing of alarm wire too far away from the window. not sure if he's right on this or not but he sure is a pain to work with.
 
I would consider if there was a fire and you didn't have an approved wire, could the insurance company deny you a new home. I've heard it happen before from an inspector. Christopher Caserta
Sr. Regulatory Engineer
ccaserta@enorthhampton.com
Ph:904-225-0360
Fax:904-225-0340
 
Status
Not open for further replies.

Part and Inventory Search