The contractor is insisting that Ld formula for tension is not applicable in columns because by doing it so, lapping is excessive for rebars with dia 32mm size. Our design department clearly specify that lapping shall be at mid height with tension splice of 1.3xLd. So that will make the lapping length of about 3.0m. But the clear height of the floor is 4.20m. So according to contractor, it is not practical to adopt such length. They want to use Ld in compression which is shorter. Please give your opinion regarding the matter.