Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Inclined Beam Connections onto flat surfaces

Status
Not open for further replies.

Ibeam

Structural
Sep 12, 2001
42
I have w8 simply supported roof beams on an incline of 5 degrees, approx. 1:12 slope. One end bears on top of a horiz. wide flange, and the other end goes on top of an 8" cmu wall.

What would be a practical bolted connection detail? Do I have to cut the bottom flange back and weld a Horizontal plate for a clean fit onto the bearing surface?
 
Replies continue below

Recommended for you

I wouldn't cut the flange. Lots of labor. Using tapered steel shims beneath the flange seems easier.
 
Won't normal shimming and grouting take care of this?
 
Thank you. It's been awhile since any building structures were thrown at me. I was thinking a little more towards the nut (top) side of the connection. Do you shim there as well? I don't remember ever doing something like that. Or does it not matter?

 
I would suggest two solutions.
You could weld a tee-shaped bearing plate which is wider than the bottom flange of your roof beam (I'm assuming it's a roof beam). The bearing plate would be bolted to the support beam.
Or you could raise the top elevation of the support beam and connect the roof beam to the web instead of bearing on top.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor