alanElec
Electrical
- Feb 14, 2013
- 78
I have a Electrical Panel feeding two chillers of FLA 1003A ,two pumps of FLA 81 A,one AHU of FLA 12 A,a Lighting DB 16 A..The incoming breaker(Motorized ACB) size for this panel is 2500 A. Busbar rating 2500 A with SC rating of 100 KA for 1 sec.Can you guys pls tell me weather the incomer breaker size is adequate?Also the consultant had already sized the transformer for this panel as 1600 KVA..Is this correct?