rockman7892
- Apr 7, 2008
- 1,172
We are bringing a new plant power distribution system online which is the reason for alot of my posts lately. I am a fairly new engineer who is trying to learn a lot of this stuff as it happens. I appreciate all of the help from this forumn.
On our main breaker we have a Multilin 750 protective relay, and a Multilin PQMII power quality meter. When looking at the currents on the Multilin, they are showing up strange for they are blinking between some current value and zero. I'm not sure if this is because I have a bad relay, or because of what I am seeing on my PQM meter which is as follows:
When looking at the PQMII meter I notice that I am getting negative kW power readings. I find this strange, so when I look at the current phasors they look strange as well. I know this negative kW reading is incorrect because I have another PQMII meter downstream measuring the exacty same load giving the exact same readings except the numbers are positive. This is why I am thinking that I may have a CT or a PT out of phase on the PQMII and ML 750 on the main breaker, which are both looking at the same CT's. Here are the readings I took off of the PQMII.
Voltge Phasors:
Vab = 4137 @ 0 deg LAG
Vbc = 4181 @ 120 deg LAG
Vca = 4172 @ 300 deg LAG
Current Phasors:
Ia = 27A @ 255 deg LAG
Ib = 27A @ 18 deg LAG
Ic = 27A @ 130 deg LAG
Three phase real power = -152 kW
Three phase Reactive Power = -130 kVAR
Three phase Apparant Power = 195 kVA
Three phase power factor = .74 LAG
I'm guessing that the CT's are out of phase with the PT's. Does this make sense?