Dear all,
I have island system with 150 kV bus. From this bus wehave 150/33 kV step down xfmr and and 150/11 kV xfmr. the 11 kV xfmr has NGR 200 amps 10 sec. the 33kV xfmr is solidly grounded.
Several times if we had fault on 33 kV the voltage dip on 33 kV side untill 3 kV and the voltage on 11 kV side also dip around 75% and trips the drives for big motors on 11kV. Some one told me thats because our system inpedance is low.
What do I need to do to increase system impedance ?
If I change my xfmr from 6.5 % Z to maybe 15 % Z is it going to be a significant change to system impedance ?
I understand that more Z to the system more electrical loss.
Adding NGR to 33 kV is not an option because the fault mostly phase to phase.
regards
Ilyas
I have island system with 150 kV bus. From this bus wehave 150/33 kV step down xfmr and and 150/11 kV xfmr. the 11 kV xfmr has NGR 200 amps 10 sec. the 33kV xfmr is solidly grounded.
Several times if we had fault on 33 kV the voltage dip on 33 kV side untill 3 kV and the voltage on 11 kV side also dip around 75% and trips the drives for big motors on 11kV. Some one told me thats because our system inpedance is low.
What do I need to do to increase system impedance ?
If I change my xfmr from 6.5 % Z to maybe 15 % Z is it going to be a significant change to system impedance ?
I understand that more Z to the system more electrical loss.
Adding NGR to 33 kV is not an option because the fault mostly phase to phase.
regards
Ilyas