In this specific instance the connected drives are "faultless", and the control DC supplies (available through the daisy-chain ribbon cable) are good - within voltage tolerence, and with acceptable ripple levels.
I have a copy of the "before" waveform (previously mentioned; the one showing a big commutation notch). Once the isolation transformer has been mounted and wired I'll save an "after" waveform, stick both into a PDF, post it to my personal web space, and plonk a URL to it in this thread. My guess is that the spurious mains fault will go away once the isolation transformer is supplying the KVR ... if my guess is wrong I'll post that here, too
![[dazed] [dazed] [dazed]](/data/assets/smilies/dazed.gif)
.
When the two lines using these Indramat drives were first installed we had a somewhat similar problem with the servo power supplies for the trimpress, except that, in those cases, the power supplies would puff the
blue smoke of death.
This problem went away after adding a 3% line reactor to the 400HP DC extruder drives, and installing isolation transformers for the press servo supplies.
My best guess, in that case, was that a press power supply (which has two axis with fairly fast start/stop motions, and another servo swinging the cutting platen) would see the line notch go down all the way to 0 volts, figure it was zero-crossing (and OK to regenerate back to the line), and blue smoke when it learned differently.
The PDF docs at my disposal don't get into the nitty-gritty (no schematics; not even adequately detailed block diagrams) to answer this assumption definitely ...