nodoubt
Electrical
- Apr 28, 2005
- 8
Application:
We have six 5hp 3ph 460V motors.
The wires are all in the same conduit trunkline back to the MCC. (longest run 225ft.) We are using
Siemens Sirius soft starters 3rw3024. We had a situation where one of the softstarters shutdown. The amperages readings for the motors were all in the proper range. To further debug, the motor leads were disconnected from the motor and from the soft starter. We were getting about 60-100VAC (T-lead to ground) on the wires. Ungrounded delta system.
Basically with all the soft starters off you may have 40mV on one set of T-leads. As you turn one soft starter on (just powering up 120VAC control) at a time you can see the voltage rising on the disconnected T-leads.
A ground wire is run to each motor. And the conduit system is continuous throughout.
I was thinking about using some type of coil or a resistor.
All suggestions are welcome.
We have six 5hp 3ph 460V motors.
The wires are all in the same conduit trunkline back to the MCC. (longest run 225ft.) We are using
Siemens Sirius soft starters 3rw3024. We had a situation where one of the softstarters shutdown. The amperages readings for the motors were all in the proper range. To further debug, the motor leads were disconnected from the motor and from the soft starter. We were getting about 60-100VAC (T-lead to ground) on the wires. Ungrounded delta system.
Basically with all the soft starters off you may have 40mV on one set of T-leads. As you turn one soft starter on (just powering up 120VAC control) at a time you can see the voltage rising on the disconnected T-leads.
A ground wire is run to each motor. And the conduit system is continuous throughout.
I was thinking about using some type of coil or a resistor.
All suggestions are welcome.