dkle40h
Electrical
- Mar 10, 2003
- 13
I would appreciate any information on motor protection, right back to the basics.
We have recently blown our second 220kW, squirrel cage induction motor in a slimes pumping operation. We have three pumps running in series to generate the required pressure head. When the slimes settle it is practise to pump water into the line using one of the pumps to get the slimes flowing. The motor in question is connected to a 525V 3 phase supply, and theoretically should draw 290A. A third motor has been installed but trips the breaker on starting. The breaker is set at 2750A. The DOL starting current is 6.9 times full load according to the manufacturer. We start using star/delta.
I am certain that the problem lies with our protection settings. The contactor can safely open 3000A, once only.
Thanks.
We have recently blown our second 220kW, squirrel cage induction motor in a slimes pumping operation. We have three pumps running in series to generate the required pressure head. When the slimes settle it is practise to pump water into the line using one of the pumps to get the slimes flowing. The motor in question is connected to a 525V 3 phase supply, and theoretically should draw 290A. A third motor has been installed but trips the breaker on starting. The breaker is set at 2750A. The DOL starting current is 6.9 times full load according to the manufacturer. We start using star/delta.
I am certain that the problem lies with our protection settings. The contactor can safely open 3000A, once only.
Thanks.