Industrial Bldg Requirement

Status
Not open for further replies.

TMEldridge

Mechanical
Sep 23, 2003
27
0
0
US
I've been trying to confirm whether or not a 400 sq ft un-manned water tank building would require fire alarm or sprinkling systems? SBCCI (georgia) does not seem to require. Its a 1 story, ground level bldg with a man door and 10ft overhead door, exhaust fan, and evaporator skid. Any ideas?
 
Replies continue below

Recommended for you

My opinion is that if the water tank building is constructed of non-combustible materials, containing non-combustible machinery/equipment, and does not represent an exposure to other important building areas, then automatic sprinker protection would not seem warranted (nor cost effective for such a small building). Perhaps only some form of passive fire detection would be necessary, with the alarm being transmitted to a constantly attended location/alarm company. Hope this helps.
 