mls1
Electrical
- Aug 15, 2002
- 133
I'd be interested in comments regarding two situations with an industrial distribution system. The system in question has a turbine generator with a GSU substation that steps 13.8kV up to 69kV. The system is high impedance grounded at the generator and the 13.8kV transformer connection is delta. Here are the issues:
1. There is a tap in the 13.8kV system to feed industrial loads. This was done with a high resistance grounded primary wye transformer. The transformer secondary is delta connected 2400V feeding a number of 2400V substations and loads. The 2400V system has a ground detection transformer with wye/broken delta connection. My question is, why not just use a delta/wye transformer to feed the 2400V system and put a high resistance ground on the wye for detection? Granted, when the generator breaker is open the 13.8kV system will be ungrounded but that is not that unusual and a wye connected PT bank can be used for ground detection (zero sequence voltage).
2. This same installation has a delta connected three phase regulator on the 13.8kV tap to the wye/delta 13.8kV to 2400V transformer. This is to help regulate the widely varying transmission voltage. We now need to add another tap to the system which will require another regulator. What I don't understand is why a delta connected regulator wasn't put at the substation the first time and the entire 13.8kV system was regulated rather than just the distribution tap. The generator regulator is currently PF control which wouldn't be a problem. I've seen LTCs on GSU transformers with no issues so I don't see any reason why a delta regulator would be a problem.
Comments would be appreciated.
1. There is a tap in the 13.8kV system to feed industrial loads. This was done with a high resistance grounded primary wye transformer. The transformer secondary is delta connected 2400V feeding a number of 2400V substations and loads. The 2400V system has a ground detection transformer with wye/broken delta connection. My question is, why not just use a delta/wye transformer to feed the 2400V system and put a high resistance ground on the wye for detection? Granted, when the generator breaker is open the 13.8kV system will be ungrounded but that is not that unusual and a wye connected PT bank can be used for ground detection (zero sequence voltage).
2. This same installation has a delta connected three phase regulator on the 13.8kV tap to the wye/delta 13.8kV to 2400V transformer. This is to help regulate the widely varying transmission voltage. We now need to add another tap to the system which will require another regulator. What I don't understand is why a delta connected regulator wasn't put at the substation the first time and the entire 13.8kV system was regulated rather than just the distribution tap. The generator regulator is currently PF control which wouldn't be a problem. I've seen LTCs on GSU transformers with no issues so I don't see any reason why a delta regulator would be a problem.
Comments would be appreciated.