HI all, I have been a very good reader of a lot of post here and would like to extend my appreciation and thanks.
I have been using IEEE 519 limits on the true PCC and we have always been compliant with it fortunately.
However, I have also been trying my best to understand and been looking for reasonable bases for applying IEEE 519 limits or figuring out specific limits we can use on buses way downstream of the TRUE PCC. There are several cases were the IEEE 519 limits are impractical when we are looking into downtream MCCs with VFDs that are significantly away from the PCC. In most cases, we apply IEEE 519 limits, spend huge cost on filters and call it a day.
However, it gives me interest to see if there are experienced folks here who can guide or help me understand if there are any withstand limits of cables, motors; and acceptable % harmonics we can establish to avoid nuisance tripping or mal-operation of relays or breakers that are less stringent than IEEE 519 limits when applied to significantly downstream of the TRUE PCC. The following are my dumb examples on what I am looking for:
- if harmonic currents flowing into the cables are 7%, this will be 107% total current (60 HZ + non-linear currents) and the cable sized to maintain 125% with de-rating should be able to withstand it.
- If harmonic voltage (THD) at the bus was 8%, this will be like 108% overvoltage assuming 100% 60 Hz voltage. If the insulation rating was greater than 108%, then the insulation would be ok
But yet, there are harmonic-generated losses which results to overheating, decrease in system efficiency and reduced design life of equipment....these are hard to quantify.
I read latest IEEE 519 and it did not address this, though it was partially discussed in IEEE 519-1992 (and later the paragraphs were deleted in the latest revision). I am assuming the standards committee were cautious of folks misapplying them if they were specified.
Bottom line, I am inquiring and asking for advice to establish REASONABLE voltage and current harmonic limits applied way downstream of the PCC where the harmonics are greater due to larger connected impedances seen at the harmonic sources.
I have been using IEEE 519 limits on the true PCC and we have always been compliant with it fortunately.
However, I have also been trying my best to understand and been looking for reasonable bases for applying IEEE 519 limits or figuring out specific limits we can use on buses way downstream of the TRUE PCC. There are several cases were the IEEE 519 limits are impractical when we are looking into downtream MCCs with VFDs that are significantly away from the PCC. In most cases, we apply IEEE 519 limits, spend huge cost on filters and call it a day.
However, it gives me interest to see if there are experienced folks here who can guide or help me understand if there are any withstand limits of cables, motors; and acceptable % harmonics we can establish to avoid nuisance tripping or mal-operation of relays or breakers that are less stringent than IEEE 519 limits when applied to significantly downstream of the TRUE PCC. The following are my dumb examples on what I am looking for:
- if harmonic currents flowing into the cables are 7%, this will be 107% total current (60 HZ + non-linear currents) and the cable sized to maintain 125% with de-rating should be able to withstand it.
- If harmonic voltage (THD) at the bus was 8%, this will be like 108% overvoltage assuming 100% 60 Hz voltage. If the insulation rating was greater than 108%, then the insulation would be ok
But yet, there are harmonic-generated losses which results to overheating, decrease in system efficiency and reduced design life of equipment....these are hard to quantify.
I read latest IEEE 519 and it did not address this, though it was partially discussed in IEEE 519-1992 (and later the paragraphs were deleted in the latest revision). I am assuming the standards committee were cautious of folks misapplying them if they were specified.
Bottom line, I am inquiring and asking for advice to establish REASONABLE voltage and current harmonic limits applied way downstream of the PCC where the harmonics are greater due to larger connected impedances seen at the harmonic sources.