ZDR1985
Mechanical
- Mar 24, 2010
- 102
Hi guys,
I am just a bit confused on this, so someone in here could enlighten me please. What is the difference between the two statements below from NFPA-2001 (Standard on Clean Agent Fire Extinguishing System).
Distribution System Section
5.7.1.1.2* For inert gas agents, the discharge time required to
achieve 95 percent of the minimum design concentration for
flame extinguishment shall not exceed 60 seconds for Class B
fuel hazards, 120 seconds for Class A surface fire hazards or
Class C hazards, or as otherwise required by the authority having
jurisdiction.
Nozzles Section
6.4.1.2* The maximum permitted time to extinguish a fire
with an inert gas agent shall be 30 seconds.
Thank you.
I am just a bit confused on this, so someone in here could enlighten me please. What is the difference between the two statements below from NFPA-2001 (Standard on Clean Agent Fire Extinguishing System).
Distribution System Section
5.7.1.1.2* For inert gas agents, the discharge time required to
achieve 95 percent of the minimum design concentration for
flame extinguishment shall not exceed 60 seconds for Class B
fuel hazards, 120 seconds for Class A surface fire hazards or
Class C hazards, or as otherwise required by the authority having
jurisdiction.
Nozzles Section
6.4.1.2* The maximum permitted time to extinguish a fire
with an inert gas agent shall be 30 seconds.
Thank you.