A few weeks ago I posted a question about this subject which seemed to cause confusion over the SI units being utilised. Since my question I have clarified it and am posting for all's info.
Inertia Constant 'H' can be defined as the ratio of stored energy at a rated speed to the rated apparant power of a given machine such:
Inertia Constant 'H' = K.E. (kW.sec)/kVA
where K.E. = 1/2.I.w^2 = 1/2.(Wr^2).w^2
=1/2.Wr^2.(rpm.2pi/60)^2
= Wr^2.rpm^2.(5.483)/1000 Joules
= Wr^2.rpm^2.(5.483)/10^6
such it follows the injertia constant
= Wr^2.rpm^2.(5.483)/10^6 kVA
This figure is related to the size and weight of the rotor and the higher the figure for a particular machine the greater it's capability in dealing with sudden increase in load and greater stability.
Regards
G