Meinkaun
Electrical
- Nov 29, 2007
- 6
Hi,...
I am working on a basic feeder protection involving a new 10/12.5 MVA ONFA 69/13.8 KV transformer. The %Z of transformer is 6.4%. I am using ETAP for simulation. Now,
When I have to input the value of inrush current, the typical value is 12 times I(full load current). Now what I am wondering, this full load current is based on 10 or 12.5 MVA because 12.5 MVA is forced air but steady state rating.
The other issue I am wondering about is that inrush current depends upon the voltage and current cycle.zero point.... That means, is there a possiblity the current might exceed 25XI(FL) for 1/2 cycle and 12XI(FL) for 6 cycle?
I would appreciate your comments.
Thanks