prc
Electrical
- Aug 18, 2001
- 2,013
It is usually reported that for small power transformers,the inrush current is 10 times full load current(If) and for large units it tends towards 5 times full load current.This data is also used for selecting protective relay settings.
My query is with respect to the meaning of this ratio. Inrush is a peaky one and we are taking the peak value of first cycle for comparison. Then we should take the peak value of If and not rms vlaue.But it seems industry is comparing the inruh peak with rms value of If.
Similarly, since inrush current value is phase value, we should take phase value of If and not line value( for delta connected windings)
What is the correct convention and is there any mention of it in standards?
My query is with respect to the meaning of this ratio. Inrush is a peaky one and we are taking the peak value of first cycle for comparison. Then we should take the peak value of If and not rms vlaue.But it seems industry is comparing the inruh peak with rms value of If.
Similarly, since inrush current value is phase value, we should take phase value of If and not line value( for delta connected windings)
What is the correct convention and is there any mention of it in standards?