Because I'm not an engineer, and I'm currently in heated discussions with an electrical engineer, I need some theoretical assistance with the following circuit.
13.8kV primary to 600V secondary, 600V secondary to 600V/4.16kV autotransformer to 4.16kV softstarter, softstarter to 4.16kV motor.
13.8kV-600V = 1MVA
600V-4.16kV = 330kVA (Actually a 4.16kV H-side, but reversed for whatever purpose rated at 45.8A)
4.16kV softstarter (designed for 600HP motor originally)
4.16kV motor (45.7FLA, 594RPM, 12 pole, 300HP)
Trying to convince them that this will not function, nor is it a conventional installation.
Currently they cannot get the shaft to turn due to loss of control voltage on the softstarter due to voltage drop incurred based on the inrush current.
It should be noted that, as designed, there was a 600V softstarter in the circuit in front of the autotransformer causing voltage collapse as well.
There are multiple issues with impedance as far as reversing an autotransformer in this fashion, as well as inrush conditions changing dramatically, but are there any expected values that I can present to this engineer that can backup my words rather than just saying "You can't do that"?
Even if they achieve spinning the shaft uncoupled, there's no way that this circuit will run loaded.
Any input would be great.
Thank you in advance.
13.8kV primary to 600V secondary, 600V secondary to 600V/4.16kV autotransformer to 4.16kV softstarter, softstarter to 4.16kV motor.
13.8kV-600V = 1MVA
600V-4.16kV = 330kVA (Actually a 4.16kV H-side, but reversed for whatever purpose rated at 45.8A)
4.16kV softstarter (designed for 600HP motor originally)
4.16kV motor (45.7FLA, 594RPM, 12 pole, 300HP)
Trying to convince them that this will not function, nor is it a conventional installation.
Currently they cannot get the shaft to turn due to loss of control voltage on the softstarter due to voltage drop incurred based on the inrush current.
It should be noted that, as designed, there was a 600V softstarter in the circuit in front of the autotransformer causing voltage collapse as well.
There are multiple issues with impedance as far as reversing an autotransformer in this fashion, as well as inrush conditions changing dramatically, but are there any expected values that I can present to this engineer that can backup my words rather than just saying "You can't do that"?
Even if they achieve spinning the shaft uncoupled, there's no way that this circuit will run loaded.
Any input would be great.
Thank you in advance.