Could anyone point me to a standard or certification for installers for specialized gases?
NFPA 55 does a great job of calling out what needs to happen; but nothing even hinted at for qualifications of installers.
NFPA 99 (covering Health Care Med Gases) specifies ASSE 6000 series installers, testers, and verifiers, but those gases (O2, Med Air, N2O) are relatively tame, at pressures of 55-100 psi.
The AWS (American Welding Society) has installer certifications for welding and brazing tasks, but nothing on general installation/testing certifications for industrial gases.
A sub-group of the CGA (the CGACB) offers certification for bulk compressed medical gas supply systems - but nothing outside that narrow area of discipline.
This project has multiple gas lines: Acetylene at 10 psig, Methane at 1200 psig, O2 at 1200 psig, UHP Argon, UHP Nitrogen, Helium, and a couple more. The opportunities for errors will be many.
Other than specifying "Shall be installed in accordance with NFPA 55", I'd like to ensure that the Contractor has a working knowledge about the systems - and dangers therein - he will be installing.
TIA.
NFPA 55 does a great job of calling out what needs to happen; but nothing even hinted at for qualifications of installers.
NFPA 99 (covering Health Care Med Gases) specifies ASSE 6000 series installers, testers, and verifiers, but those gases (O2, Med Air, N2O) are relatively tame, at pressures of 55-100 psi.
The AWS (American Welding Society) has installer certifications for welding and brazing tasks, but nothing on general installation/testing certifications for industrial gases.
A sub-group of the CGA (the CGACB) offers certification for bulk compressed medical gas supply systems - but nothing outside that narrow area of discipline.
This project has multiple gas lines: Acetylene at 10 psig, Methane at 1200 psig, O2 at 1200 psig, UHP Argon, UHP Nitrogen, Helium, and a couple more. The opportunities for errors will be many.
Other than specifying "Shall be installed in accordance with NFPA 55", I'd like to ensure that the Contractor has a working knowledge about the systems - and dangers therein - he will be installing.
TIA.