Does anyone know if anyone makes such a product and/or options?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
You are misinterpreting the need and use of instantaneous-only breakers. The ONLY valid use for them (in North America) is as a COMPONENT of a factory assembled, tested and listed combination starter. Period. End of story. You CANNOT use an instantaneous-only breaker for ANY other purpose. They are not UL listed, ever, they are only UL Recognized Components (backward UR symbol), because they must be used WITH something else, in this case a UL listed thermal overload relay. So you can’t possibly have a situation where a “motor itself is also subject to Instantaneous only protection” here in NA, there is no such rule or requirement. So because there is no such valid use scenario for an MCB with instantaneous-only trips, nobody makes one.BlackJackJacques said:My application is for a critical motor control circuit where the motor itself is also subject to Instantaneous only protection.