Hi, Folks,
Inst. settings are very sensitive. Sometimes I try to avoid it for the main and branches. Per code, CEC or NEC, we are not allowed to disable them. So what I normally do is to set Inst on Main higher than the branch fault currents(Max.available), which is reduced by impedance in between. But sometimes on some high voltage systems, it is very hard to do the co-ordination study because the impedance makes little deference between fault currents on two levels of buses. Who have a better solutions?
thank you in advance.
Inst. settings are very sensitive. Sometimes I try to avoid it for the main and branches. Per code, CEC or NEC, we are not allowed to disable them. So what I normally do is to set Inst on Main higher than the branch fault currents(Max.available), which is reduced by impedance in between. But sometimes on some high voltage systems, it is very hard to do the co-ordination study because the impedance makes little deference between fault currents on two levels of buses. Who have a better solutions?