EddyWirbelstrom
Electrical
- Feb 17, 2002
- 216
How is the instantaneous element of a current limiting circuit-breaker such as a motor circuit protector set ?
eg. If a motor with a LRA of 6 x FLA and a starting power-factor of 0.2 has an initial symmetrical rms inrush current of 2 x LRA = 12 x FLA, then half a cycle after motor energization the motor asymmetrical rms current could be ( worst-case assuming motor start at voltage zero crossing ) 15 x FLA and the peak (crest) current would be 26 x FLA.
Is the current limiting circuit-breaker instantaneous element calibrated ?
Is the required instantaneous setting :
15 x FLA / 0.8 for 20% minus tolerance of Instantaneous element
or
26 x FLA / 0.8 for 20% minus tolerance of Instantaneous element
See attached spreadsheet for calculations.
eg. If a motor with a LRA of 6 x FLA and a starting power-factor of 0.2 has an initial symmetrical rms inrush current of 2 x LRA = 12 x FLA, then half a cycle after motor energization the motor asymmetrical rms current could be ( worst-case assuming motor start at voltage zero crossing ) 15 x FLA and the peak (crest) current would be 26 x FLA.
Is the current limiting circuit-breaker instantaneous element calibrated ?
Is the required instantaneous setting :
15 x FLA / 0.8 for 20% minus tolerance of Instantaneous element
or
26 x FLA / 0.8 for 20% minus tolerance of Instantaneous element
See attached spreadsheet for calculations.