An IR test from the switchgear through the power cables is much easier and does not require determing and reterming field cables (as well as reinstalling Raychem insulation for high voltage leads). But the cable IR can be an order of magnitude lower than the motor IR, masking possible problems in the motor until they become very pronounced.
Maintenance Dept argues that if they can achieve the minimum required insulation resistance with cables connected(100 Megaohms temp-corrected for higher-voltage form-wound machines)
I argue Since motor failures are much more frequent than cable failures and therefore end up costing more, it seems that extra effort to disconnect the cables is worth the time to get an earlier warning which may enable us to avert a problem.
How do you approach this?
Are there any standards that provide a basis for one approach over ther other?
Maintenance Dept argues that if they can achieve the minimum required insulation resistance with cables connected(100 Megaohms temp-corrected for higher-voltage form-wound machines)
I argue Since motor failures are much more frequent than cable failures and therefore end up costing more, it seems that extra effort to disconnect the cables is worth the time to get an earlier warning which may enable us to avert a problem.
How do you approach this?
Are there any standards that provide a basis for one approach over ther other?