Insulation resistance testing on 230v equipment

Status
Not open for further replies.

lyledunn

Electrical
Dec 20, 2001
122
Just as a matter of interest, when testing equipment with smpsu and filtering equipment, can an insulation resistance test at 500v from a PAT tester cause damage? PAT tester links phase and neutral and tests between these 2 conductors and earth.
 
Replies continue below

Recommended for you

It is ususally not appropriate to test smpsu and filters at 500 v, because as already advised it can cause damage, and would also fail the test. Other circuits such as the power save mode on some computer monitors use a bridge of 4 x 330 ohm resistors which will return a value of 0.3 to 0.4 Mohm form a tied line neutral to earth test.
It is more reasonable to skip the insulation resistance test and perform a functional earth leakage measurement. This value (U.K) should be less than 3.5 miliamps.

Regards,

KVKEV

 
smpsu- switched mode power supply unit.
PAT - Portable Appliance Test

Regards,

kvkev
 