majan
Electrical
- Aug 1, 2005
- 5
We used to have procelain string insulators in system where in pf and impulse withstand levels are defined per disc (like we use 5 disc in 33KV and 3 in 11KV)Now since silcone ruber insualtors is under proposal I would like to know How the pf & impulse values should change in specification. WIll it be a direct multiple of 5 to per disc value for 33KV ? I think NOT. but then how to define new value OR is it simply the system values based on insulation coordination?
pls throw light and Thanks