Bilegan
Electrical
- Oct 7, 2008
- 47
One (1) vertical section of each bus of my existing MV switchgear, 4000A, 13.8kV, 60Hz. is to be modified to replaced the old air blast MV circuit breaker with new VCB. Since the CT's of the existing relays device 50/51 and 50G with zero sequence CT are under rated, we opted them to be removed as well and replaced with new individual relays, i.e., device 50/51 and 51N with only new 3 CT's.
The existing MV switchgear to be modified will feed a new MV switchgear, 1200A, 13.8kV, 60Hz., secondary selective, N.O. bus tie VCB, and have auto transfer scheme. Each of the incomer protection relays are device 51 and 51N only, no instantaneous overcurrent relay device 51 option.
A 3x1/C-240sqmm,XLPE,AWA per phase power cables between existing and new MV switchgears, without separate grounding wire. The distance between existing and new switchgear is approx. 1.5 kM, power cables will be installed underground of approx. 500m and then emerged aboveground in cable tray for a distance of approx. 1000m.
My senior suggest that there should be inter tripping control circuit between existing and new switchgear. According to him, an additional tripping relay device 94 and lockout relay device 86 shall be added for the inter-tripping requirement.
He also suggest to change the proposed new device 51N with 50G with a separate zero sequence CT in the existing MV switchgear.
I am totally confused, my understanding is, a transfer trip is applicable only between 13.8kV switchgear and 4.16kV switchgear via step-down trafo, 13.8kV pri. and 4.16kV sec.
I need your opinion guys!
Regards,
Bilegan
The existing MV switchgear to be modified will feed a new MV switchgear, 1200A, 13.8kV, 60Hz., secondary selective, N.O. bus tie VCB, and have auto transfer scheme. Each of the incomer protection relays are device 51 and 51N only, no instantaneous overcurrent relay device 51 option.
A 3x1/C-240sqmm,XLPE,AWA per phase power cables between existing and new MV switchgears, without separate grounding wire. The distance between existing and new switchgear is approx. 1.5 kM, power cables will be installed underground of approx. 500m and then emerged aboveground in cable tray for a distance of approx. 1000m.
My senior suggest that there should be inter tripping control circuit between existing and new switchgear. According to him, an additional tripping relay device 94 and lockout relay device 86 shall be added for the inter-tripping requirement.
He also suggest to change the proposed new device 51N with 50G with a separate zero sequence CT in the existing MV switchgear.
I am totally confused, my understanding is, a transfer trip is applicable only between 13.8kV switchgear and 4.16kV switchgear via step-down trafo, 13.8kV pri. and 4.16kV sec.
I need your opinion guys!
Regards,
Bilegan