EE7860
Electrical
- Jul 18, 2006
- 10
I have an interesting question if any one can help.
2 identical compressor motors with the following data.
600HP, 2300V, 390RPM, 152FLA
Both were run uncoupled to check the amps.
One being fed from Delta-Wye transformer with the following data
12470V-2400Y/1383
2000/2240(OA) KVA, %Imp 5.24, transformer tap is set at 12160V. The motor running amps are approximately 104A on all three phases.
Second Transformer is Delta-Delta 13200-2400V, 1500KVA, %Imp 5.43, Transformer tap is set at 12540V. The running amps recorded are approximately 65A on all three phases.
Both transformers are ungrounded, The system voltage is 12470V. In the past motors were exchanged but the amps stayed with the transformer, in other words on Delta-Wye configuration motor pulls more amps.
Any suggestion? I thought power requirement will be the same in any case and the motors will run identical on both systems.
2 identical compressor motors with the following data.
600HP, 2300V, 390RPM, 152FLA
Both were run uncoupled to check the amps.
One being fed from Delta-Wye transformer with the following data
12470V-2400Y/1383
2000/2240(OA) KVA, %Imp 5.24, transformer tap is set at 12160V. The motor running amps are approximately 104A on all three phases.
Second Transformer is Delta-Delta 13200-2400V, 1500KVA, %Imp 5.43, Transformer tap is set at 12540V. The running amps recorded are approximately 65A on all three phases.
Both transformers are ungrounded, The system voltage is 12470V. In the past motors were exchanged but the amps stayed with the transformer, in other words on Delta-Wye configuration motor pulls more amps.
Any suggestion? I thought power requirement will be the same in any case and the motors will run identical on both systems.