BONILL
Structural
- Mar 9, 2010
- 74
I have an interior 8" thick cmu wall used only for division purposes (non load bearing). The wall spans 5.80m. (between the top of concrete slab below to bottom of concrete slab above). It is connected to the concrete slab below with dowels.
For pressure out of plane I considered the following:
1. W = 10 psf minimum wind load for interior walls.
2. W = 0.40 x SDS x I x Wc for seismic.
My design tells me that I should connect the cmu wall at the top to the slab above using dowels, and with this simply supported condition, I should use #3 @ 16" o.c. as flexural steel. I am also using a 8" x 12" beam at mid height of the wall and a 8" x 12" beam at the top of the wall. I'm also prescribing 8" x 8"columns at 5m. o.c.
Am I missing anything?
For pressure out of plane I considered the following:
1. W = 10 psf minimum wind load for interior walls.
2. W = 0.40 x SDS x I x Wc for seismic.
My design tells me that I should connect the cmu wall at the top to the slab above using dowels, and with this simply supported condition, I should use #3 @ 16" o.c. as flexural steel. I am also using a 8" x 12" beam at mid height of the wall and a 8" x 12" beam at the top of the wall. I'm also prescribing 8" x 8"columns at 5m. o.c.
Am I missing anything?