I have a control strategy that has been through multiple reviews and has finally cleared through the MOC approval process we have at my company.
It has landed on my task list to implement these controls.
There are a couple of issues that I've noticed with this control strategy and the one that I would very much appreciate any feedback from folks here concerns closing a valve on the output of a pump pair that has no minimum flow spillback.
This question is primarily about the pump and whether or not there is a risk of damaging the seals and potentially causing a fire.
Typically I would expect to simultaneously shutdown the pump when it is required to automatically initiate a command to close the valve on the pump discharge, but this is nowhere to be found in the design that has been approved for this change.
Operations has advised that it is their fundamental practice to manually stop pumps when the pumps' discharge valve is closed by an automated interlock.
Not so surprisingly, this might explain part of the causes that I've heard about this plant having a fair amount of reliability issues with its pumps.
In my opinion deadheading a centrifugal pump flowing butane is not quite what I would consider a recognized and generally accepted good engineering practice.
Thanks in advance for taking the time to share your thoughts on this subject.
It has landed on my task list to implement these controls.
There are a couple of issues that I've noticed with this control strategy and the one that I would very much appreciate any feedback from folks here concerns closing a valve on the output of a pump pair that has no minimum flow spillback.
This question is primarily about the pump and whether or not there is a risk of damaging the seals and potentially causing a fire.
Typically I would expect to simultaneously shutdown the pump when it is required to automatically initiate a command to close the valve on the pump discharge, but this is nowhere to be found in the design that has been approved for this change.
Operations has advised that it is their fundamental practice to manually stop pumps when the pumps' discharge valve is closed by an automated interlock.
Not so surprisingly, this might explain part of the causes that I've heard about this plant having a fair amount of reliability issues with its pumps.
In my opinion deadheading a centrifugal pump flowing butane is not quite what I would consider a recognized and generally accepted good engineering practice.
Thanks in advance for taking the time to share your thoughts on this subject.