I have a 480V 1MW utility-paralleled generator that is tripping on phase differential.
It will go months between events where it operates fine at all levels of load, but then a couple trips will happen in close succession. There doesn't appear to be any common factor between trips events.
The generator protection is always picking up ~200A of differential between the generator neutral and the leads on "C" phase. It sounds like a ground-fault, right? The problem is that this unit has a high-impedance ground with 59N and this element has never picked up. So if there is a differential, where is the current going?
Additionally, I've done insulation-resistance and winding surge testing on the generator and the leads at 2kV and everything looked fantastic, where if there was a ground-fault I would really expect it to flush out at 4X the RMS operating voltage.
Unless there's a problem with the 59N circuit or the differential CTs, I'm sort of at a loss to explain this. And if it were a metering problem, I wouldn't tend to expect it to be intermittent.
Any ideas?
It will go months between events where it operates fine at all levels of load, but then a couple trips will happen in close succession. There doesn't appear to be any common factor between trips events.
The generator protection is always picking up ~200A of differential between the generator neutral and the leads on "C" phase. It sounds like a ground-fault, right? The problem is that this unit has a high-impedance ground with 59N and this element has never picked up. So if there is a differential, where is the current going?
Additionally, I've done insulation-resistance and winding surge testing on the generator and the leads at 2kV and everything looked fantastic, where if there was a ground-fault I would really expect it to flush out at 4X the RMS operating voltage.
Unless there's a problem with the 59N circuit or the differential CTs, I'm sort of at a loss to explain this. And if it were a metering problem, I wouldn't tend to expect it to be intermittent.
Any ideas?